We are having a protracted discussion on the sizing of the GEC where there are multiple grounding electrodes. We have a hypothetical installation where the main service panel, with 500kcmil SE conductors, has a grounding electrode conductor connected to a Ufer ground and then a ground rod. Would the connection from the panel to the Ufer be a #4 copper and the connect from the Ufer to the rod be a #6? Or since the connection to the Ufer is not the "sole connection" would the GEC from the panel to the Ufer be a #1/0 (full size GEC)
And, if there was an additional connection from the rod to a water pipe would all the connections, panel to Ufer to rod to water pipe need to be #1/0 full size?
And, if there was an additional connection from the rod to a water pipe would all the connections, panel to Ufer to rod to water pipe need to be #1/0 full size?