I have a very strange application that a project manager brought to my attention at an industrial plant. Recently, the project manager installed a 100kW Generator on a 120/208V service with two feeds; one that feeds UPS power for server equipment, and the second that powers HVAC for the server room. The problem is what the Generator OEM provided him. For some reason, they gave him a 4-pole, 225A ATS and a 3-pole, 125A ATS, so now, I have 4-pole switch for one load, and a 3-pole for the other load. I have never seen such an installation before, and wanted to know for sure that there isn't a code issue.
I did confirm with the project manager that they did not install a grouding electrode conductor at the generator which you would normally be for separately derived system, but he only bonded the equipment grounding conductor to the grounded electrode system due to the existence of the 3-pole ATS which still inter-connects the neutral back to the distribution panel, to make it non-separately derived.
I've reviewed the NEC, and the only thing I can see us doing is to follow NEC 700.7(B) for signs to make sure someone knows about the potential shock hazard if the GEC is removed at the MDP.
See attached for reference to what I'm seeing here. Again, the generator OEM doesn't see any issue, but it sure is funky to me. Feedback is appreciated.
I did confirm with the project manager that they did not install a grouding electrode conductor at the generator which you would normally be for separately derived system, but he only bonded the equipment grounding conductor to the grounded electrode system due to the existence of the 3-pole ATS which still inter-connects the neutral back to the distribution panel, to make it non-separately derived.
I've reviewed the NEC, and the only thing I can see us doing is to follow NEC 700.7(B) for signs to make sure someone knows about the potential shock hazard if the GEC is removed at the MDP.
See attached for reference to what I'm seeing here. Again, the generator OEM doesn't see any issue, but it sure is funky to me. Feedback is appreciated.