Transfer switch - question discussing the neutral
ct1911guy
CT
Hey all, first post here, and rather new to my Journeyman status (please don't beat me up too badly:D). I am installing a transfer switch betweem my main 200amp 120/240 panel and a 100 amp sub panel. Now after being all high and mighty and installing everything, I realized that the neutral is NOT switched in the transfer switch. Now shouldn't the transfer switch be switching the two hots and the neutral?:? Could the neutral in the transfer switch carry an unbalanced load out on the street side neutral when using a generator? Or am I just confused about the whole thing here? I'd really like to go about this the best and safest way possible. Any help would be greatly appreciated.
Thanks.
If the neutral is not switched it?s not a separately derived system. That changes the way the bonding is done.
What is in the top conduit between your two panels in the picture?
Welcome to posting.
A large majority of the transfer switches do not switch the neutral.
The neutral being connected to the utility does not provide a path for the current to follow.
Man made electricity seeks it's own source, not other sources. No problem. Just be sure there is no bond between ground and neutral at your generator.
top conduit
top conduit
the top conduit is a fubar. i wasn't thinking when I installed it. I am going to put a trough there instead for all the splices.
generator bonding
generator bonding
So in order to make this work i would have to unbond the neutral from the generator so that the GFCI wouldnt trip. But then if i were to use the generator as a stand alone for a jobsite, i would have to rebond it? this kinda seems like a silly way to do things. i feel like i should just go out and get a different transfer switch.
Now the beating starts :D
Manual Transfer or Automatic ?
Generator size ? Portable ?
let the beating begin!
Manual Transfer Switch
Generator size - haven't bought it yet - looking at a Generac xg8000 and yes its portable, i am open minded to another generator within the same price range
Looks like a neat job.
(please don't beat me up too badly).
You only get to use that line once here. After that we beat the crap out of you.:p
What splices are you anticipating ? If you're using the top conduit to bring over existing branch circuits, make sure you bring over the neutrals for each circuit as well. The neutrals have to originate in the panel the branch circuit is fed from.
I would look into purchasing a generator that didn't have the 120/240, 30A output GFI protected
That is what has to happen if you stay with a portable under 15Kw.
Beat, Beat Whip,Whip
Can't find a transfer switch
I've been looking for days and cannpt find a 3 pole manual transfer switch. All I can find is 2 pole with a neutral bar. Anyone know of a reasonably prices 3/4 pole manual transfer switch or a generator without a gfci protected L14-30?
I would leave the existing ATS, is surely is easier to bond then remove the bond as needed for temporary use than replace the ATS.
Assuming this is not a daily occurrence.