Is there an industry standard or a code reference for acceptable voltage drop on a fire alarm circuit? I am reviewing shop drawings and the manufacturers calculations came back with a 20% voltage drop. 20V down to 16V.
This may be familiar to a lot of you here; when projects I was involved in were required to have no more than 10% voltage drop, we would measure the voltage at the terminals of the power supply and see a typical 26.7 volts. We would use this figure in our calculations to give us a little more headroom (2.67 volts vs. 2.40 volts).
had to repost,, time limits and all prevented me from doing so ,,ignore above, see below
Yes, and you wont find your answer until you find a """"very good"""" DC power guy (ie- me
the formula is
11.1 x LL x A / VD
You must look to the manuf spec or calculate the OCP size in amps.
once that is done, you inject that amperage or 80% of the amperage into the formula to determine the circular millimeters of copper required to power the device.
Lets say your brand x fire panel has a 400w, 24v name plate rating (some of these can operate at -48vdc as well as a ups backed 120vAC so double check your options)
inject ohms law and you arrive at 16.6A, 16.6A / .8 = approx a 20A dc fuse size.
next find out how far away in cable feet the power run is.
lets say its 20' one way or 40' loop (you have to account for both the + and - legs because its dc)
Now we can calculate the wire size required for a 40'Loop 20A dc circuit with a constant of 11.1 for copper in the DC power industry , and account for no less than a .875 volt drop (you could allow 1v if you you want)
so, here we go,,
11.1 x 40 x 20 / .875 = 10,148 circular millimeters of copper required to properly engineer this circuit per Telcordia and Bellcore standards (both of which are well known in the DC Power industry).
the same calculation applies if you de-rate to 80% OCP but you come up with 8118cmil of copper required which is still pulling you to #10.
you could get the wire size down in my example "if" this device is the only DC power item and nothing downstream of the fire panel requires the 24v dc source. If so, you could use 80% ocp and a 1v or even a 2v allowable loss but you have to explain your engineering if questioned.
In my honest opinion, if your 24v is "not" coming from a 24v battery back up DC power plant be it small or large, there is no reason to engineer as aggressively as i have here, i figure worse case all the time.
SO, i would power your new panel in this situation with a #10 1pair cobra copflex non halogen CT rated wire and using the 75degC column.
I have such a hard time with my AC guys getting them to understand why on the last project the 100A -48V circuit got a #2 +/- wire but yet on this other project i had them cable with 2/0.
again, the formula is
11.1 x loop length x amps / allowable voltage drop
you wont find any of this in the NEC, they barely have just begun to define anything DC power
the op supplied a question and i had to inject some knowns in order to explain the standard DC power math.
I do not know what the 20v device is,, it could be a wall wart powering the fire panel, it could be a downstream supervisory circuit the fire panel is controlling.
there were too many unknowns so i just started with some made up assumptions to support the OP so it could be applied in the same way where he is delivering the dc power from and to, thats all.
if he is powering up a Fire Alarm Panel off a 24v source, by all means allow for no more than a 1v drop especially if the 24v source is a battery back up 24v source. Could he get away with more of an allowable voltage drop, sure,, just be able to explain the engineering like we all have to for liability sake.
As for fusing,, i would assume we all make our best attempt to fuse each DC circuit no matter how small it is. We fuse right down to the 1/8A and even lower. In DC you want to fuse any power lead possible but most people think little loads will be fine because the wire becomes the fuse link,,, then the fire suppression dumps ect ect.
im probably just a little too cautious but its good practice in the dc industry.
if i knew more exactly of what the op's application was, then we all might a better answer.
Since this was mentioned earlier, one cannot power a fire alarm panel from a wall wart.