You can also purchase 240V rated heaters with a higher wattage rating then needed, then operate at 120V with the calculated voltage drop to give you the wattage you want.
I don't see that solving any voltage drop issues. If you need 300 watts of heat you will still need 2.5 amps of current if the voltage remains the same. Extending the life of the element is about the only benefit of operating it at a lower voltage than it is rated for.