230.40 Number of Service-Entrance Conductor Sets.
Exception No. 2: Where two to six service disconnecting means in separate enclosures are grouped at one location , one set of service-entrance conductors shall be permitted to supply each or several such service equipment enclosures.
?and supply separate loads from one service drop or lateral?
I understand this part but when you add this sentence to qualify the rule I?m lost as to what that means. This exception is commonly used to allow double lugging a meter and installing two distribution panels side by side to supply the same dwelling or building. Most commonly done with 400 amp services supplying two 200 amp distribution panels.
My gut feeling on this was that it really was written to allow separate metering of the water heater load on a different rate. Or in commercial a standard rate and a heating load rate.
Exception No. 2: Where two to six service disconnecting means in separate enclosures are grouped at one location , one set of service-entrance conductors shall be permitted to supply each or several such service equipment enclosures.
?and supply separate loads from one service drop or lateral?
I understand this part but when you add this sentence to qualify the rule I?m lost as to what that means. This exception is commonly used to allow double lugging a meter and installing two distribution panels side by side to supply the same dwelling or building. Most commonly done with 400 amp services supplying two 200 amp distribution panels.
My gut feeling on this was that it really was written to allow separate metering of the water heater load on a different rate. Or in commercial a standard rate and a heating load rate.