Applicable details:
New Concrete Slab House
NEC 2008
I have a job where we parralel feed USE-2 in 2-2" conduits from Utility Transformer to 400 amp meter base (no disconnects) and terminated into meter base lugs. Then we ran 2-2" Conduits under the concrete slab about 60' to two separate 200 amp panels that are side by side. We used USE-2 in these conduits with the thinking the conduit under the slab is exterior. We turned the Siemens panels so the main breaker was down so we did not have to run the wire to the top.
The inspection failed as the inspector said we had a termination point (meter base) and we should have changed the wire type we used to feed the panels. He cited I believe Section 338.12 of the code and specifically pointed to prohibited uses section "not for Interior Use". I did not feel this was an interior use as it is terminating in the panel and not going any further than that.
Am I incorrect in my thinking?