Sorry if this sounds like a silly question, but since we've only been on the 2008 for a year I haven't had enforce this.
Is a Equipotential bonding ring required around a self contained, above ground fiberglass spa?
Under the 2008 NEC yes.
There is a TIA for the 2011 NEC that eliminates the requirement for the equipotential bonding grid for self contained spas, here is what it says;
Exception No. 2: A listed self-contained spa or hot tub that meets all of the following conditions shall not be required to have
equipotential bonding of perimeter surfaces installed as required in 680.26(B)(2):
(1) Is installed in accordance with manufacturer?s instructions on or above grade.
(2) The vertical measurement from all permanent perimeter surfaces within 30 horizontal inches (76 cm) of the spa to the top
rim of the spa is greater than 28 inches (71 cm).
HERE is a link to the TIA.
Chris