correctI am just trying to get some things straight. In a class 1 div 2 area
if it does not spark, You don't need X proof boxes fittings or Flex.
correctBut you do need threaded steel conduit,
only between enclosures that are required to be explosionproof and the seal,Xproof unions
seals are required at boundries and enclosures that are required to be explosionproofconduit seals
correctand you can use liquidtight,
not requiredclass1 div 2 boxs and condulets?
Unlike Division 1 [NEC 501.15(A)(2)], where seals are virtually mandatory, seals for a purged or pressurized protection technique in Division 2 take some judgment and analysis [NEC 501.15(B)(2) Ex No. 3]. NFPA 496 is a critical reference for making the call. Type Z (Class I, Division 2 to unclassified) pressurizing requirements are fairly minimal. See NFPA 496, Sections 4.8 and 5.4.Some of the equiptment is purged and I would think you should seal comming out of that?