A residential service uses a 1/0 THW aluminum conductors. The minimum size aluminum grounding electrode conductor for this installation would be a? Section 250.66 says a #6, but the answer that was given is a #4??
I'll take a stab at that. The book is wrong. :happyyes:
I think you missed with your stab.:p You need a #4 for aluminum conductors, #6 is for copper.
Wait a minute. Dennis might be correct. The question is unanswerable since the grounding electrode is not defined??
I might agree as we don't know if it's copper or Al. I use AL all the time for the Service but never use Al for the GEC.
With a 1/0 AL SE, do you know of any instance in which you can use an AL GEC smaller than #6...??? :happysad::happysad::happysad:
I didn't say unanswerable I said the book was wrong because #4 is not the correct answer. I believe my answer is correct.
I now agree, regardless of SE being mentioned, I see what you are saying. The 1/0 AL being used for the residential service would be for 125 A, accordingly the GEC could be #6 AL per 250.66.