I need clarification. I have a transformer with a five wire system (3 phase conductors, a grounded conductor, and a grounding conductor) going to a MDP. Can the transformer and the MDP both be bonded?
Did you mean EGC when you said "grounding conductor"?Can the transformer and the MDP both be bonded?
Did you mean EGC when you said "grounding conductor"?
As to your question of bonding the neutral at both locations, you can only do that if there will never be any conductive path that may occur as to provide a parallel current path of the grounded (neutral) conductor. See 250.30(A)(1) Exception 2
Roger