We have recently run across some issues in the field with the AHJ citing the VAV boxes not having 42" clear in front of the control panel (boxes contain 480V electric heaters and 277V fans). Typically most jurisdictions have just required sufficient "access" to the mechanical equipment and not "working space" as required for electrical equipment such as switchgear, panelboards, MCCs and similar. That said, I certainly can see where a VAV box would be "likely to require examination, adjustment, service, or maintenance while energized", if nothing else to check voltages.
From experience, this is always the grey area of 110.26 as by default equipment above the ceiling is usually accessed off of a ladder and thru a 2'x2' suspended metal ceiling grid which means you almost never have more than 2' clear area anyway.
Any thoughts on this?
From experience, this is always the grey area of 110.26 as by default equipment above the ceiling is usually accessed off of a ladder and thru a 2'x2' suspended metal ceiling grid which means you almost never have more than 2' clear area anyway.
Any thoughts on this?