Does anybody know how to determine an MCCB instantaneous trip setting? I haven't done this in a couple years. I was thinking 10 or 15x the FLA?
Thanks.
Thanks.
Does anybody know how to determine an MCCB instantaneous trip setting? I haven't done this in a couple years. I was thinking 10 or 15x the FLA?
Thanks.
Does anybody know how to determine an MCCB instantaneous trip setting? I haven't done this in a couple years. I was thinking 10 or 15x the FLA?
Thanks.
To be compatible with the coordination study, it should be set at just above the inrush current of the largest connected load on startup. If the breaker is in an MCC then I would follow the old Westinghouse recommended procedure: 1. Raise the inst dial to max. 2. Start and stop the motor. 3. Lower the setting 1 notch each time you restart motor until the breaker trips, then raise the dial 1 notch. 4. Restart motor to prove no-trip. This will be the final setting. This setting should match the trip curves in the study and also takes into account cable impedance, as well.