jefcon1
New member
- champaign, il
Why would a hot 120v 30amp circut burn up wire, xfmr, and get past 2 breakers (primary and secondary) before finally blowing a 200 amp fuse in the switchgear?
I have heard people say that about GE but never about Square-D.
Oh please, none of those statements have any justification. If GE breakers did not work they would be out of the business, and FP is made by the same company as Square-D. Show me any proof that any of those have high failure rates.
It is not a failure of one device or another. The breaker standards do not specify the level of the instantaneous trip for small breakers. The instantaneous trip point for a Square D QO breaker is lower than any of the competitive products. The GE is the highest. They all do what the UL standards say them must do, but there are differences.Oh please, none of those statements have any justification. If GE breakers did not work they would be out of the business, and FP is made by the same company as Square-D. Show me any proof that any of those have high failure rates.
I know you are very biased towards GE,
Shorting out a breaker and listening to the sounds is not even close to being a test of how a breaker functions or when it trips. Primary inject a breaker and compare to manufactures TCC's, only way to test a breaker.To compare apples to apples, The Orange box used Square D up until Nardelli took over, then they switched to GE (wonder why?):roll: If you short a 20 amp circuit out in the Square D store, you get a small pop, then it's tripped, short out a 20 amp circuit in a GE store, the pipes rattle, then it trips. I'm not saying GE does not trip, it just allows a higher current through before tripping.