stickboy1375
- Litchfield, CT
I'll go, ummmm the pipe was to short and he didn't know any better. (they could have flipped it around) Or he was in Indiana![]()
You can already see it bending... only a matter of time.![]()
Did you leave them a note with a business card on their door?
Lol, we do work for them, I just noticed it today... Im not saying anything... its probably been that way for 10+ years...
It's been that way since you installed it. I see.
Do you always post photos of your work for others to ridicule?
I have a job coming up where I will go with a 5' piece of emt right above the meter panel and then transition to a full 10' stick of ridgid so the coupling is not near the roof.
Is that how you guys do the job or do you use all ridgid and thread the short piece?
NO! Use RMC the entire length, also, just buy a thread less connector if you don't own a pipe threader.
An EMT fitting nas straight threads, and will not properly seat in the panel hub.
Neither would an SE connector but there are millions of those installations too. Good point.
Which actual code violation are we looking at with the threads being an issue?
230.28 Service Masts as Supports.
Where a service mast is used for the support of service-drop conductors, it shall be of adequate strength or be supported by braces or guys to withstand safely the strain imposed by the service drop. Where raceway-type service masts are used, all raceway fittings shall be identified for use with service masts. Only power service-drop conductors shall be permitted to be attached to a service mast.