I'm an inspector. Contractor installed small PV system on the roof of a large commercial office building built in 1972. Inverter is on the top floor beneath the panels, next to a subpanel with an EGC. They crimped the GEC to the EGC, which made me cringe. The crimp that cringes. I like it.
Electrician on a TI in the building laughed when I said we need to find the GEC to irreversibly bond to. He claims in buildings this old there were no electrodes required (California). The building itself is fed off a service in another building on site, the main D panel in building with the PV doesn't have a ground bus bar and nothing that is obviously a GEC. It's on the 2nd floor, fed directly from the other building.
Contractor wants to bond to building steel, but we have no way to verify whether this building steel meets the requirements for building steel to qualify as an electrode. I could make him bond to the water pipe in the basement, but that's a lot of work to put him through. Transformers can be bonded to the water pipe anywhere in the building for an electrode connection, so maybe we can allow this as 'alternate methods and materials'. Sprinkler pipe is close by too.
I think we should have him bond to sprinklers, building steel, and water pipe at a main trunk line, not a branch line, and leave it at that.
Thoughts?
Electrician on a TI in the building laughed when I said we need to find the GEC to irreversibly bond to. He claims in buildings this old there were no electrodes required (California). The building itself is fed off a service in another building on site, the main D panel in building with the PV doesn't have a ground bus bar and nothing that is obviously a GEC. It's on the 2nd floor, fed directly from the other building.
Contractor wants to bond to building steel, but we have no way to verify whether this building steel meets the requirements for building steel to qualify as an electrode. I could make him bond to the water pipe in the basement, but that's a lot of work to put him through. Transformers can be bonded to the water pipe anywhere in the building for an electrode connection, so maybe we can allow this as 'alternate methods and materials'. Sprinkler pipe is close by too.
I think we should have him bond to sprinklers, building steel, and water pipe at a main trunk line, not a branch line, and leave it at that.
Thoughts?