110.26 (C) (2) requires (with exceptions) more than one exit when "equipment rated 1200 amperes or more" is located in a room. The problem is that the word "equipment" is both single and plural.
I know that if I have a single switchboard rated 1200A or more this applies.
What if I have three 400A panels or six 200A panels or twelve 100A panels?
I have an AHJ saying that because the total capacity of the "equipment" (plural) is 1200A, I need to comply.
Can anyone offer an NEC citation that provides clarification?
I know that if I have a single switchboard rated 1200A or more this applies.
What if I have three 400A panels or six 200A panels or twelve 100A panels?
I have an AHJ saying that because the total capacity of the "equipment" (plural) is 1200A, I need to comply.
Can anyone offer an NEC citation that provides clarification?