Is it a violation to backfeed a circuit breaker and use it as a main on a MLO panel? Seems lile the main lugs would be energized when this is done.
Is it a violation to backfeed a circuit breaker and use it as a main on a MLO panel? Seems lile the main lugs would be energized when this is done.
Is it a violation to backfeed a circuit breaker and use it as a main on a MLO panel? Seems lile the main lugs would be energized when this is done.
I believe that as long as the panel is listed to do it that way you should be OK. Cutler Hammer Ch panels are the only ones I've ever done this on and you have to install the hold-down bracket to hold the "main" breaker in place.