Voltage drop calcs. for motor feeders w/ remote VFD
steveve1
Tucson, AZ
Hello All and Merry Christmas from chilly Arizona, I'm wondering how having a VFD mounted a distance away from the motor affects voltage drop calculations. For example: A 10hp motor @ 480v, 100' feeder length. At nominal voltage I assume a load of 14a. VD calcs indicate a drop of 4.8v with #12cu conductors. Will the conductor size be adequate through the range of the applied voltage to the motor from the VFD? I have an installation with several VFD controlled motors, varying distances and HP. Is there a general "rule of thumb" or will standard VD calcs apply regardless of the VFD control?
Thanks in advance....and Happy Holidays!
I've never taken into consideration that it was powered by a VFD, just distance wire size and amperage.
You calcullations are based on 60 cycles. I suspect the output from the drive is much higher that that.
Did you actually measure the VD? Cable impedance at the higher frequency will increase.
Others use one size higher of its conductor ampacity with VFD control to compensate for harmonics.