Article 110.26(D) Illumination Control

Status
Not open for further replies.

mdl75134

New member
Location
Dallas, TX
Does this requirement allow the installation of a manual switch on the load side of the occupancy sensor to manually bypass the automatic shut off feature when work is being performed in an electrical room. Also, is the installation of manual timers allowed.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does this requirement allow the installation of a manual switch on the load side of the occupancy sensor to manually bypass the automatic shut off feature when work is being performed in an electrical room. Also, is the installation of manual timers allowed.

If the manual switch can bypass the sensor then there should be no issue. It is compliant.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Dennis, the purpose here is to ensure that the lights don't automatically shut off while someone is in the room working.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Does this requirement allow the installation of a manual switch on the load side of the occupancy sensor to manually bypass the automatic shut off feature when work is being performed in an electrical room. Also, is the installation of manual timers allowed.

A switch to bypass the Occ sensor would be OK.

A timer to bypass the Occ sensor would not meet the requirments, IMO, since it would still automatically turn off the lights after a set time.
 