Dimming duplex outlet...

Status
Not open for further replies.

dwellselectric

Inactive, Email Never Verified
Got into a little argument with the bosses son. He wanted me to replace a switch that controls a typical duplex receptacle with a dimmer. I told him I believe you can't do that unless you install a special outlet. I could be mistaken but can't find it in the code. Can anyone help me please?
 
You win. 404.14(E) Lutron makes a "dimmer " recep. and a matching cord cap. As we all know this is violated all the time. IMO it is very poor practice and leads to problems.
 
Got into a little argument with the bosses son. He wanted me to replace a switch that controls a typical duplex receptacle with a dimmer. I told him I believe you can't do that unless you install a special outlet. I could be mistaken but can't find it in the code. Can anyone help me please?
See what happens when a receptacle is dimmed with a 600w dimmer and a vacume cleaner is plugged into it:jawdrop:
 
As we all know this is violated all the time. IMO it is very poor practice and leads to problems.
It may be done in your area all the time but I have never seen it done.

Roger
 
I don't know for sure, but I think this was legal until fairly recently. I'd say the 80's but that's just a guess.

I guess that's not very recent after all is it?

or it could have been 2002.
 
Last edited:
I don't agree with it. Say someone plugs something like a computer or an LED tv into the outlet imo a stupid move to install a dimmer on an outlet

dSilanskas, If you listen to the boss's son by installing the dimmer, end user could have the benefit of putting his/hers computer on the power saving mode!!!
 