mshields
Senior Member
- Location
- Boston, MA
I've got a campus distribution system at a hospital where the service to the facility is 13.8kV. From the service switchgear (S&C), I've got a dozen or so pad mounts rated 13.8kV delta to 480Y/277V. Here's my questions:
Since the service is upstream of the transformers, each transformer needs to have a grounded conductor or neutral AND a ground conductor to the 480V switchboard. True?
Also, the ground conductor is a "secondary bonding jumper" and therefore, needs to be sized in accordance with Table 250-66 and not 250-122.
Just looking for a sanity check here. I know that the last statement would be true for an ordinary dry type, I'm just wondering if the fact that the transformer is more than 600V has any impact on this.
Thanks,
Mike
Since the service is upstream of the transformers, each transformer needs to have a grounded conductor or neutral AND a ground conductor to the 480V switchboard. True?
Also, the ground conductor is a "secondary bonding jumper" and therefore, needs to be sized in accordance with Table 250-66 and not 250-122.
Just looking for a sanity check here. I know that the last statement would be true for an ordinary dry type, I'm just wondering if the fact that the transformer is more than 600V has any impact on this.
Thanks,
Mike