hardworker
Senior Member
House has 200amp service. The panel is installed on an interior wall of the house, so by local code it needed a 200amp breaker disconnect on the outside of the house by the meter.
The 200amp disconnect breaker keeps tripping.
The house had a new heatpump system with emergency heat installed this past summer. I found inside the air handler unit it had been installed using awg #6 - 3 conductor with grd and awg #10 - 3 conductor with grd on a 60amp 2 pole breaker and 30 amp 2 pole breaker respectly. This is correct, except the extra conductor. Neutral is not needed on these 2 pole applications. The installer had just clipped the white neutral on both the 30 and 60 and left copper exposed on both.
This HVAC installer did the same with the neutrals inside the panel.
Per the homeowner, a handiman was in the panel lately and told the home owner two of the neutrals were not hooked up, so he installed them onto the neutral bar. Of course he did not trace them.
Heating season came and the outside disconnect started tripping. Apparently the #6 neutral in the HVAC was shorting against the housing of the unit.
I cleaned up the mess, but my question is the following?
Why did not the 60amp breaker in the panel not trip. Why did it hold and the disconnect outside was the one to trip? Why did not the 200amp panel main not trip?
The 200amp disconnect breaker keeps tripping.
The house had a new heatpump system with emergency heat installed this past summer. I found inside the air handler unit it had been installed using awg #6 - 3 conductor with grd and awg #10 - 3 conductor with grd on a 60amp 2 pole breaker and 30 amp 2 pole breaker respectly. This is correct, except the extra conductor. Neutral is not needed on these 2 pole applications. The installer had just clipped the white neutral on both the 30 and 60 and left copper exposed on both.
This HVAC installer did the same with the neutrals inside the panel.
Per the homeowner, a handiman was in the panel lately and told the home owner two of the neutrals were not hooked up, so he installed them onto the neutral bar. Of course he did not trace them.
Heating season came and the outside disconnect started tripping. Apparently the #6 neutral in the HVAC was shorting against the housing of the unit.
I cleaned up the mess, but my question is the following?
Why did not the 60amp breaker in the panel not trip. Why did it hold and the disconnect outside was the one to trip? Why did not the 200amp panel main not trip?