Bennington
Member
- Location
- Illinois
If a trough has 480V running through it [spliced or not] should it be labled catagory 0?
If a trough has 480V running through it [spliced or not] should it be labled catagory 0?
Thanks for your response. I did read the faq. There is a lot of good information there, however, I didn't find anything that addressed my question. The reason for my question is on a jobsite I found a trough labled catagory 0 containing 480V circuits. When I looked in NFPA70E under 600V equipment cable troughs it puts the catagory at 1, However note 3 states that with less than 10ka of short circuit current available it can be dropped by 1. I guess a better question would be other than <10ka of short circuit current is there any other reason it could be dropped to 0?