A coworker and I were having a disagreement this morning about the definition of a feeder and a specific application. The scenario was that we have a fused disconnect and a subpanel to install at the opposite end of the building as the MDP. My point was that it is ok to pull the conductors for the sub panel and disco in the same conduit as long as you de- rate the conductors and don't exceed the max fill of the conduit. He said that this would be a code violation since we would be pulling feeders to the sub panel and a branch circuit to the disconnect. The definition of a feeder according to the NEC does not apply to this as far as I can see, since they are both fed from the mdp on their own breakers. . I don't see where this would be prohibited.