GTCAM
 - Latrobe, PA
Hello All,
This is an expansion of the local little league complex. We added a concession stand and field lighting. I have volunteered to help with the electrical. Please see the attached two drawings. The first is existing, the second is proposed (by me). I appreciate any comments you can give me on the design. Below are a few questions that come to mind:
1. is it ok to leave the 400A disconnect, and only upsize if I have trip problems?
2. is it ok to tie the new circuits at the 400A disconnect, and if so, is it ok to do this via adding lugs in the disconnect? Is there a better way?
3. what would the proper grounding arrangement be at the equipment building?
Thanks in advance for the help!