scotteng
- Apollo Beach, FL
- Professional Engineer
I have project with a 400A, 120/208V, 3-phase, 4-wire service served by a pad-mounted transformer. The meter is post mounted, self-contained 320A located adjacent to a pad-mounted transformer that is remote from the building. NG bond occurs in the main at the building and we are showing connection to two driven ground rods and all available grounding electrodes at the building. We are also calling for a driven ground rod and #4 Cu ground the meter per POCO requirements. The issue I have is that the AHJ have made a comment to remove the ground at the remote meter and to make all connections to ground at the main disconnect, citing 250.30(A)(7). This would effectively mean that we will install an EGC in our service lateral (never done that before) and I have question about what size that conductor would need to be. Any thoughts or comments are appreciated.