Heating Elements
Chamuit
Grumpy Old Man
Texas
I am going to install some heaters (heater assembly) for a vat. Currently there is a single phase heater being used right now. It is on a 50A circuit with a 50A res/40A fla contactor to open an close the circuit.
The customer ordered a three heater assembly to replace the single unit. Each heater is a 25A single phase unit with the OCP @ 50A according to the tag.
So if I wire them up to a three phase circuit as the wiring diagram shows. (Doing AB, BC, CA which evenly distribute the loads.) I get 6kW * 3 = 18kW
18kW ? 240V 3P = 43.37A
At 125% I get 54A.
So, do I use a 60A breaker and 60A res contactor?
Or, do I follow the single phase ratios and go 75A and 75A?
At 125% I get 54A.
You don't need to factor by 125% if the heaters will typically not be energized continuously 3 hours or more, i.e. 50A equipment. If typically energized continuously 3 hours or more, use 60A equipment.
What about 427.4? I'd say he needs 60A equipment even if the equipment isn't normally energized continuously for 3 hrs or more.
The tank is probably 500 gallons or so and they have to re-heat it in them mornings in the summer and keep it warm in the winter. It is a continuous load. I had looked in the 420-ish sections myself and came away with the 60A ratings.