No. NEC 210.12 requires AFCI in dwelling units only, and this is not a dwelling unit. 210.18 goes on to require AFCI in dorm rooms that have permanent provisions for cooking, and your building does not.
 
No, 210.12 (A) applies to dwelling units and dorm rooms that do not meet the definition of dwelling unit would not require AFCI protection.

Chris
 