The panel is a generaor sub-panel so there is no ground bus. Thanks to all who reply.
I have run into a situation where I have run out of places to land neutral wires on a neutral bar. Can I install two neutral wires under one screw? The panel is a generaor sub-panel so there is no ground bus. Thanks to all who reply.
If the neutral bar rated for double wire connection then you can, or you can install a grounding bar and move all of the equipment grouding conductors (egc) to this new grounding bar to make room in the neutral bar,
This is true for many lugs but it is not true for the neutral bar.If the neutral bar rated for double wire connection then you can, or you can install a grounding bar and move all of the equipment grouding conductors (egc) to this new grounding bar to make room in the neutral bar,
I think wanted to make sure you had the panel grounded, which you do but not with a ground bus jus a lug or something similar. You could add another neutral bar- they make them.Mike Whitt, post #3- All of the ground wires stay in the main panel. The only ground connection in the sub panel is the one from the main panel to the sub panel box and onto the generator.