O.K. here's the deal.  3-pole 30amp 480v breaker is tripping on overload.  A phase-8 amps, B phase-8 amps, C phase-42 amps.  I'm thinking that there's a bad connection in the field somewhere causing the imbalance but I'm not sure.  This is a brand new install, so the contractor is contractually responsible for any issues that arise within 1 year.  Based on the as-builts, each phase should be drawing around 18 amps.  What else would cause these type of readings?  Bad ballast?  Thanks in advance.
	
		
			
		
		
	
				
			
				