Does anyone still make branch breakers <100A, or anything else for that matter, that only have a 60 deg C rating? Everyone that I looked at has 60/75 now, so 110.14(C)(1) allows sizing from the 75 deg column even though it is <100A.
Does anyone know of a device that doesn't have a 60/75 terminal? Maybe snap switches and receptacles?
Does anyone know of a device that doesn't have a 60/75 terminal? Maybe snap switches and receptacles?