Sandyman
- Evansville, IN USA
In Unit 9 question 51 is an optional method calculation. The correct answer is 1/0 awg AL according to the instructor, although I can only come up with 103A which would be #1 awg Al?
The question and my calculations;
A dwelling unit has 2,330 qu ft of living space. In addition, there is 900 sw ft of porch and 400 sw ft of carport (not a garage) with the following;
Waste Disposal ( 1 KVA)
Dishwasher (1.5 KW)
Trash Compactor (1.5 KVA)
Water Heater (6 KW)
Range (14 KW)
Dryer (4.5 KW)
A/C Unit (5 hp 230V)
Baseboard Heat (Four at 2.5 KW each)
Use the optional method to determina what size aluminum conductors are required for the 120/240V, single-phase service?
General lighting and rec (2,330 x 3) = 6,990VA (porch and carport are not included)
Small appliance and laundry = 4,500
Waste Disposal = 1000VA
Dishwasher = 1500VA
Trash Compactor = 1500VA
Water Heater = 6000VA
Range = 14,000VA
Dryer = 4500VA
Total VA = 39,990
A/C Unit (5 hp at 230V) Table 430.248 5hp = 28A = 6,440VA 220.82(C)(1)
Baseboard Heat (Four at 2.5 KW each) 10,000VA x 40% = 4,000VA 220.82(C)(5)
Use the largest of the 2 loads 6,440VA
NEw Total VA = 46,430VA
First 10,000VA at 100%
Balance at 40% (36,430 x 40% = 14,572VA)
Calculated net load 24,572VA / 240V = 102.4A
Table 310.15(B)(6) 110A = #1awg AL
Is this correct or am I missing something?
Dishwasher (1.5 KW)
Water Heater (6 KW)
Range (14 KW)
Dryer (4.5 KW)
Dishwasher = 1500VA
Range = 14,000VA
Dryer = 4500VA
Total VA = 39,990