I'm having a liitle trouble trying to get hold a towns local Electrical Inspector to see if he'd be strick on using 1/0 SER aluminum for a 100 amp sub panel. Usually I'd install a 100amp sub panel from a main service panel using #2 SER service cable, and just install a 90 amp breaker to meet the 75c columb of art.310-16. Acording to the NEC and many local inspectors, any cables ( including romex) leaving the 1st distribution panel, must meet the derate cable of the 60c columb. This is why i can install a 4/0 SER from a 200A service disconnect to the 1st main dist. panel. I think for conductors up to #10 gu cu, the amp ratings are higher for derating purposes. 1/0 alum, is not stocked by most supply houses, and #1 SER is non existant, and 3-3 or 2-3 romex copper way too expensive for most jobs for a sub panel. Not sure but; To meet the code entirely; even the main feeder from a service disconnect to a sub panel is supposed to be derated to the 60c columb, because it being a shiethed cable assembly, but most inspectors are letting it go. Not surewhat to make of that??
Any clarification appreciated;