Transformer powering Contactor.

Status
Not open for further replies.

aptman3

Member
I am using a 24v transformer with an output of 40 VA to open and close 3 individual 2-pole 20amp contactors. Does anyone know how many VA each contactor requires to operate? Right now everything is functioning fine but I want to make sure I am not stressing out the transformer. Thank You!
 
You should be able to get the "pull in va" and the "holding va" from the contact manufacturers spec sheet.
 
You should be able to get the "pull in va" and the "holding va" from the contact manufacturers spec sheet.

If you please explain further how the above data may be used,it would be very nice on your part.
 
Last edited:
I am using a 24v transformer with an output of 40 VA to open and close 3 individual 2-pole 20amp contactors. Does anyone know how many VA each contactor requires to operate? Right now everything is functioning fine but I want to make sure I am not stressing out the transformer. Thank You!
As Don has pointed out, there is a difference between pull-in and hold-in VA. The pull in is generally the much higher of the two but lasts usually not more than a few tens of ms. If your transformer is managing to pull the contactors in, I would think it unlikely that is being stressed by the running VA.
 
Also be careful of the type of transformer you are using. Cheap 'doorbell' transformers have poor voltage regulation and thus do not have high 'pull in' capability. The common 'furnace' transformer is usually fine when you are turning things on all at one time. A machine tool (also called a control power) transformer has the largest capacity for 'pull-in' and 'seal-in', tand can easily handle loads turing on/off while other loads remain on.
 
http://forums.mikeholt.com/showthread.php?t=141653&highlight=sola

Try the reference above, if I did it right. The OP transformer sounds like what is used on the typical older home heating system and will most likely differ somewhat in its capabilities.

Jump to Kwireds post 10.

Thanks.I just wanted to know the formula for calculation of transformer VA,given coils pull in VA.

Actually these ratings are required for not damaging the transformer but to prevent contactors chattering due to low voltage on start up.
 