titan1021
- Northern California
I had a former employer (EC) that required that we sell a service change anytime we came across a service panel that had burning and pitting on the bus bar, at the breaker connection point. We were prohibited from doing any work on the panel once we discovered burning or pitting on the bus bar. We removed the damaged breaker and advised the homeowner that the panel had to be replaced, as required by code.
I can see his position from a liability standpoint for his company, just not clear if his approach is sound and based on fact.
He insisted that this was required by 110.12(c) Integrity of Electrical Equipment and Connections.
"There shall be no damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent, cut, or deteriorated by corrosion, chemical action, or overheating"
In researching this in the forums, it seems like most people are just removing the burned breaker and using other spaces in the panel, and in some cases are just installing a new breaker right back in the same burned location. (which is shocking to see that a licensed electrician would do such a thing)
I would just like to get clarification on this issue from other electricians that have been in the trade longer than I have.
Any advice is greatly appreciated.
Thank you
Thank you