Hi everyone.
There's a camp that's been wired and rewired throughout the years.
There's a 400 amp 3 phase 4 wire service (high leg) which comes overhead from the utility to a shed where a ct cab and two (3 phase 200a) disconnects are. There is also a 100a mb single phase panel and a 100 2 pole breaker to feed a
house. There is no grounding of the service at this point, and it looks like they grabbed for a neutral for the 100 amp panel and the 100 amp breaker from the service ground in the ct cabinet. From the 200 amp disconnects they feed back
up and out overhead for north camp area and the south camp area.
There are no neutrals (grounds) in the disconnects, and the feeds going back out to supply the camp go through a rusty box that I can't get open and can only "assume" that they lugged the bare wire of the ariel cable to the box (the wiring
method in the shed is rigid conduit , metal troughs, and boxes).
All the wiring to the buildings (structures, pavilions) are fed by 4 wire (?triplex) - 3 phase (insulated) with ground (bare). At the building and or pavilion, they tapped to a phase and ground, or two or three phases and ground depending on
their needs.
At the structure, they would drop to a breaker (or main brk panel) and drive a ground rod (or go to a water pipe if there was one in that structure or to a driven pipe) and bond to the bare of the arial cable dropped to that location (for a
neutral).
Basically, it looks like they dropped a meter(ct) for the utility company then wired the camp as if they were the utility company...
If I where to ground the service "at" the utility shed (there is no water pipe), I would have to create my own grounding electrode system. If I go back overhead or below grade to feed the camp, how should I address the stuctures that have water piping going to them?
Did I mention there's a large in-ground pool at this camp? What a mess.
Thank you for your insight.
Rich
There's a camp that's been wired and rewired throughout the years.
There's a 400 amp 3 phase 4 wire service (high leg) which comes overhead from the utility to a shed where a ct cab and two (3 phase 200a) disconnects are. There is also a 100a mb single phase panel and a 100 2 pole breaker to feed a
house. There is no grounding of the service at this point, and it looks like they grabbed for a neutral for the 100 amp panel and the 100 amp breaker from the service ground in the ct cabinet. From the 200 amp disconnects they feed back
up and out overhead for north camp area and the south camp area.
There are no neutrals (grounds) in the disconnects, and the feeds going back out to supply the camp go through a rusty box that I can't get open and can only "assume" that they lugged the bare wire of the ariel cable to the box (the wiring
method in the shed is rigid conduit , metal troughs, and boxes).
All the wiring to the buildings (structures, pavilions) are fed by 4 wire (?triplex) - 3 phase (insulated) with ground (bare). At the building and or pavilion, they tapped to a phase and ground, or two or three phases and ground depending on
their needs.
At the structure, they would drop to a breaker (or main brk panel) and drive a ground rod (or go to a water pipe if there was one in that structure or to a driven pipe) and bond to the bare of the arial cable dropped to that location (for a
neutral).
Basically, it looks like they dropped a meter(ct) for the utility company then wired the camp as if they were the utility company...
If I where to ground the service "at" the utility shed (there is no water pipe), I would have to create my own grounding electrode system. If I go back overhead or below grade to feed the camp, how should I address the stuctures that have water piping going to them?
Did I mention there's a large in-ground pool at this camp? What a mess.
Thank you for your insight.
Rich