Jack Reyes
New member
- Location
- Farmington, MN, USA
In an application where a PLC uses a 16 point relay output module to switch 120VAC solenoids with each relay module having a 10A total output rating, is there a requirement to fuse each individual solenoid output or is it sufficient to fuse only the output module? The solenoid cables would be 18AWG/3C so I belive that fusing just the output module would mean that I could not go any higher than a 7A fuse, is this correct. I am confused on how this circuit is viewed by the NEC. Is it considered a power circuit, control circuit, class 1, ect.
If you have a remote panel, say within sight of the main panel disconnect, with multiple output modules in it would I bring multiple 120VAC circuit for each output module or just one large circuit and divide it up at the remote panel? An electricain I am speaking with says in that case he would prefer the small multiple circuits (All derived from the same single phase control transformer). I am trying to figure out the best way to handle this.
If you have a remote panel, say within sight of the main panel disconnect, with multiple output modules in it would I bring multiple 120VAC circuit for each output module or just one large circuit and divide it up at the remote panel? An electricain I am speaking with says in that case he would prefer the small multiple circuits (All derived from the same single phase control transformer). I am trying to figure out the best way to handle this.