2 Romex's in one connector

Status
Not open for further replies.

Dexie123

Senior Member
Hey all,

I feel dumb asking this but here it goes.

I had a co worker wire about 35 recessed lights. I wasn't there to watch him do the work but when I returned I noticed he had wired all of them (except for the endline lights) with one romex connector and put two 14/2 romex in each connector. MUCH to my chagrin.

Anyway I'm assuming this is against the listing but I'm hoping maybe I'm wrong. I'm in NJ. Do you think I'm going to get shot down for this install?

Thanks
 
Which romex connector? It sounds like a good possibility of you being wrong...typically you can fit 2 12/2 or 14/2 through one nm, romex clamp connector, but without knowing the exact connector used, it's a tough question to answer.
 
Find the similar connectors that are listed for two cables. Have the part number ready to give the inspector. If you seem to have your stuff together the inspector is not going to waste his time wondering if you actually have the ones "approved" by the "authority".

Most of the time, I choose the one that's been tested by UL and approved...but sometimes the fitting is too simple to reject a brand because UL didn't bother to test it. The whole assembly is basically 3 pieces of metal plus two screws.
 
An Arlington NM74 lets you install (2) 14-2 to 10-2 cables. You can also install (2) 14-3 cables in one fitting.

NM74.jpg


http://www.aifittings.com/products/line-drawings/NM74.pdf
 
Last edited:
I believe the Arlington black button fittings allow (2) 14/2 or 12/2 flat cables per connector or (1) 14/3 or 12/3 round cable per connector in a 1/2" KO.
 
Have been seeing 14-3 flat cables recently. Now they are going to have to have them all re tested to accomodate those:)
 
That's exactly what I was thinking of doing Jaylelectric! Haha.... Thanks everyone for your responses and advice. All very good.
 
I've been through this issue. In my case, it was the multitude of cables that had to enter the top of a panel.

The UL WHite Book will tell you that the 'smallest unit of packaging' will have the listing of the cable combinations for which the connectors are approved. In my case, the connectors were the type that have a clamp with two screws. The box they came in specifically listed twl #12-3 cables as approved. Inspector withdrew his objection.
 