- Windsor, CO NEC: 2023
- Hospital Master Electrician
Do I need to bond around concentrics for an EMT containing a 480Y/277 circuit entering a metal wireway?
Yes, see 250.97
This is explicit, but doesn't apply to wireways IMO.UL White Book said:CONCENTRIC OR ECCENTRIC KNOCKOUTSAll boxes with concentric or eccentric knockouts have been investigated for bonding and are suitable for bonding without any additional bonding means around concentric (or eccentric) knockouts where used in circuits above or below 250 V, and may be marked as such.
What does "and is listed for grounding" mean?UL White Book said:Metallic wireway installed in accordance with the product markings and manufacturer?s instructions is suitable for use as equipment grounding conductors, and is Listed for grounding.
Here's what I am looking at:
I would say with 95% certainty it does not.I don't know if the first part applies to wireways or not.
I don't think the second part is talking about concentric or eccentric knockouts but rather the wireway in general is acceptable for use as an equipment grounding conductor.
Also read the exception that follows.
If the wireway is listed for the KO to be used for bonding in this application then you do not have to have additional bonding methods.
He didn't say if his his KO's were listed for grounding as per the exception, so my answer to the the OP question would still be the same.
Am I suppose to assume?
Okay - but it says "and is listed for grounding" - what does that mean?
I figured the whole thing means the wireway is just as much of a grounding conductor as a metal raceway is, but concentric/eccentric KO's are likely a different issue.
Another one that comes to mind are raised square covers for receptacles, why don't they just come out and tell you if they are approved for grounding and you don't need a separate EGC jumper. It' like pulling teeth to get an answer.
Attach your ground wire to the 4" square box, then to the recptacle. Are you saying that
the AHJ required a seperate ground wire ?
No, I'm saying that you don't need an EGC jumper to the recep. if the cover is "approved" as a grounding means. See 250.146(A). How do I know it is approved? Kinda like George's question of wireway concentric KO's, how do you know at a moments notice in the field?
The first question I asked myself is a wireway listed as an egc. I see nothing in metal raceways that says it is although I suspect some may be listed that way. If it isn't listed as an means of grounding as emt is then wouldn't we have to bond no matter what the voltage. I suspect that a wireway is just a large jb but where do we find if it is listed as a ground.
How about the quotes from the white book that George posted in post #4?
add: as long as the wireway is listed it should meet those requirements.