mobile home feeders versus underground residential distribution (mhf /urd)

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
expanding on master's reply slightly. URD which does not carry any additional ratings (such as RHW), is a cable designed for utility distribution and is not recognized by the NEC. As such it can not legally be used for installations under NEC jurisdiction.
 