Just learned about this one.  I see some major pitfalls here.  Please review the wording of this section. If someone else here has an electronic copy please paste it so that others don;t have to go to the text.
Basically a single pole switch location would be pretty straight up. What about locations with 3 way and/or 4 way switches. Residential would be especially difficult. It is obvious to me that from now on, in commercial you might as well stub up conduit at all switches to avoid complications. But Say you have a set of 3 way switches. Location one. Do you run a 2 wire carrying hot and neutral, and a 2 wire carrying the two travelers. If so, then go to the second location. Would you need to intercept the travelers at the same location that the switch leg terminates so that you could reconfigure later on? This switch outlet my not even be capable of being energized with a hot leg, so why bring a neutral down to it? The section does state "the grounded conductor for the controlled lighting circuit shall be provided at the switch location." So do you bring down a 2 wire for travelers and 2 wire for switch leg and neutral, or do you suppose they only mean for you to bring a neutral to the first box? This, of course would not make sense to me, because, the purpose of facilitating occupancy sensors (OCC) could quite possibly require OCC's in both switch box locations. I won;t evn get in to the problem with 4 way switches, or if you have multiple circuits, 3 way switches and ganged switches in one box. WHAT A MESS!