- Licensed Electrician
I'm not gonna be Sancho Panza for you. You are on your own tilting at this windmill.
			Is there such a term?
Why is it not a Supply Side Bonding Jumper?
I understand what the intent probably was, but don't you think the wording is kind of wide open?
Your diagram does show two grounding electrodes which are required to be bonded together to for the grounding electrode system, per 250.50. As Mike Whitt tried to point out (with in error is his reference) 250.53(C) says that the bonding jumper used to connect the grounding electrodes together to form the grounding electrode system...shall be sized in accordance with 250.66.
That is the bonding jumper that is in your diagram. There is no need to size that jumper at 12.5% of the ungrounded conductors size, because it is not an equipment bonding jumper per 250.102.
Is the conductor between the steel and the water pipe a Supply Side Bonding Jumper?
"250.102(C) is for equipment bonding jumpers on the supply side of the service."
My 2011 doesn't say that. The term EBJ isn't in the whole section, skimming through.
Again, I think we all agree on the intent, but I think they stuffed the SSBJ into the NEC in a hurry and didn't notice the little things.
I cannot agree...... I agree with you, under the 2011 definitions, there is a good argument that 250.102(C) applies to the bonding jumpers in the grounding electrode system.
2011 hasn't been adopted here either...so I just have a draft copy, not the final copy.
Isn't the title of section 250.102 still "Equipment Bonding Jumpers"????
If so then nothing in 250.102 would apply to bonding jumpers in the grounding electrode system.
But there is no general provision under (C). Goes directly to (C)(1) which is titled, as I so noted earlier, "Size for Supply Conductors in a Single Raceway or Cable."No, the title has been changed to "Bonding Conductors and Jumpers", and the title of 250.102(C) has been changed to "Size - Supply-Side Bonding Jumper".
This is a "grounding electrode conductor" and therefore according to table 260.66 it can be 3/0. You need not go any larger.
"Bonding Conductors and Jumpers", "Size - Supply-Side Bonding Jumper".
not a grounding electrode conductor, it is a binding jumper.
I suppose it could be more redundantThat's pretty solid; but it could be better.
I can live with that. One of the problems with art. 250 is the terminology. And they keep adding to it under the false belief that it makes things clearer.ha ha ha............
WIRE!