petersonra
- Northern illinois
- Semi-retired engineer
Does working in a panel where all connections are "fingersafe" prevent expose of a worker to dangerous voltages?
If the inside of the panel meets IP20 "finger-safe" requirements in accordance with IEC 60529, then there are no "exposed" live parts as defined by NFPA 70E and PPE requirements may be reduced accordingly.
Again, if a worker is not "exposed" to hazardous energy as defined, NPFA 70E protection requirements do not apply.
Steve,
What if you are using tools? It is my understanding that finger safe does not prevent you from touching energized parts with tools, so in my opinion, if you are using tools in a panel with finger safe terminals you are exposed to energized parts.
Steve,
NPFA70E Handbook: 2012 : Article 100 : Exposed said:... If the equipment has ventilation openings, wires and tools could be inserted through the ventilation holes and contact energized conductors; therefore, the level of exposure is based on the task and associated tools and equipment. ...
It is my understanding that using insulated tools does not remove the requirement to use voltage rated gloves.In my experience, in countries where the concept of "finger-safe" does exist you would never use a bare, uninsulated tool like we do here in the US. I could insert any of my Wiha screwdrivers into a finger-safe screw terminal and it would maintain its finger-safe status with no energized parts exposed. The new generation of CAT rated test leads with shrouded tips are also designed to extend the finger-safe rating to an inserted, energized probe.