225 Kva transfomer Wire Size
Part-Time
Houston, Texas
i have a 225 Kva transformer (delta) supplying it with 480/277 (primary) the out put will be (Secondary)240/120
what size wire should the supply to the transformer Be ?
Look at 450.3(B) and the corresponding table. Without more information it is impossible to answer you directly. What size OCPD do you have on the primary side of the transformer?
Pete
The FLI for the primary side would be 271 amps but you have decisions to make in what protection scheme you are going to use based upon the loads served by the transformer. Table 450.3(B) gives you many options.
The primary OCPD could be set as high as 250% of the primary FLI if primary and secondary OCP are provided.
Thats why I said it comes down to the loads being served and the NEC isn't going to design the system. The NEC only dictates the parameters of your design.
Pete
For protection of the transformer that is correct. Pay particular attention to the notes following table 450.3(B)
Pete
To use the 350 kcmil conductor from a 350 amp OCPD you will have to do a load calculation. 350 kcmil is only rated at 310 amps at 75 degrees Celcius but per 240.4(B) you MAY be able to do this.
Pete
As noted, your approach should be to 1st calculate your loads. Ignoring the "inrush" factor, you might be able to use conductors/overcurrent protection less than the max allowed by Code if that's your intent.
Here. a 225 kva is most commonly fed by a 500 kcmil on a 350 amp breaker.