retfam
Member
- Location
- California
In California the intersystem bonding termination is somewhat new to us.  I can read 250.94 and see how this should be installed, but my question is, does this prohibit the continued practice of grounding the communication ground to a ufer.  Let me explain.  You would typically see a ufer with 3 bond clamps on it.  1 for the grounding electrode conductor, and 2 other for your communication wires.  With this new requirement, if a contractor wants to still provide the 2 communication bonds to the ufer, does the code prohibit that.  Does the communication bonds ("bonding for other systems") require they be put on this new external intersystem bonding?  I would still require the installation of the intersystem bonding, but it would be empty in the example I used.
	
		
			
		
		
	
				
			 
				
 
 
		