T
		T.M.Haja Sahib
Guest
The problem here is you showed both L1 and L2 as having 120V each at the same time........The other arrangement is series .........
There is no problem.The problem here is you showed both L1 and L2 as having 120V each at the same time........
This is how it gets described. Not 120, 0, -120.XPWR054-120
Power transformer for a 120V, 60Hz. line to 240V (120-0-120) at 100mA center tapped and 24V (12-0-12) at 2A center tapped.
If what you says is true,then L1 and L2 are at the same potential at any instant (for example 120v at the instant shown in your drawing) and so the two voltages L1-N and L2-N are in phase and so the two currents add in the neutral.There is no problem.
Look how the 0V ends of the windings are connected and the orientation of the windings in each of the two diagrams.
They are not the same. And intentionally drawn as they are precisely to illustrate the difference.
An ad from the internet.
The drawings aren't of a frozen instant in time and you are wrong to interpret them in that way. They are circuit arrangements.If what you says is true,then L1 and L2 are at the same potential at any instant (for example 120v at the instant shown in your drawing)
	Your diagram itself speaks the truth:The voltage vector V1-N acts from V1 to N.The voltage vector N-V2 acts from N to V2.So the two voltages V1-N and N-V2 are in phase.But V1-N and V2-N are out of phase by 180 degree.But you are left with the Hobson's choice of voltages V1-N and N-V2 only.You can not make use of voltages V1-N and V2-N here.The drawings aren't of a frozen instant in time and you are wrong to interpret them in that way. They are circuit arrangements.
This is the time relationship:
Single phase.So if this was the secondary of a transformer, how many phases would it be?
Brilliant deduction. It's what I have been saying ad nauseum.But V1-N and V2-N are out of phase by 180 degree.
No, you're not.But you are left with the Hobson's choice of voltages V1-N and N-V2 only.
Of course you can. Never heard it being informally referred to as two hots and one neutral?You can not make use of voltages V1-N and V2-N here.
See V1-N voltage vector 120v is directed from L1 to N.N is grounded and its voltage is 0v.N-V2 voltage vector is directed from N to L2.Its magnitude is -120v.These two vectors V1-N and N-V2 are in phase.One is 120v vector(V1-N) and another is -120v vector(N-V2).If N-V2 voltage vector is reversed,it becomes 120v vector(V2-N). So if the potential at L1 is 120V,the potential at V2 would also be 120v,both with respect to N.So the two currents from L1 and L2 add in it.But this does not actually happen here.Only the voltages V1-N and N-V2 voltages act here so that the neutral current is the difference of two line conductors.This is borne out even by your circuit in post #119.(The voltage marking at L2 should be changed to -120v,though)Brilliant deduction. It's what I have been saying ad nauseum.
No, you're not.
Seems that you are changing your stance on this.See V1-N voltage vector 120v is directed from L1 to N.N is grounded and its voltage is 0v.
The correct potentials in your 'more usual arrangement'above is L1=240v(with respect to L2), N=120v(with respect to L2) and L2=0V.It does not matter 'N' is grounded or not.
Please do not change the course.Please place your objections to post #152.(by the way,in response to above, please remember any one line may be considered at 0V potential and the potential of other lines can be measured/calculated.)Seems that you are changing your stance on this.
From your post #95 we get this:
As a matter of information, the V abbreviation should be upper case.
More free education for you.![]()
No, my first example was only two loads, one connected L1-N and the other connected L1-L2. I asked for the relationship between the voltages and the currents.
Then I asked for the same information except with 3 loads.
Following your notation at the N point of the sources, a KCL (which effectively says current leaving a node must equal the current leaving a node) equation would be Ia=In+Ib.
Are all of your voltages and currents 'in phase' with each other? Have values changed simply because a neutral point exists?
It's too much of a muddle to provide a coherent response.Please place your objections to post #152.
See V1-N voltage vector 120v is directed from L1 to N.N is grounded and its voltage is 0v.N-V2 voltage vector is directed from N to L2.Its magnitude is -120v. These two vectors V1-N and N-V2 are in phase.One is 120v vector(V1-N) and another is -120v vector(N-V2)