Look at 338.12(A)(2)
There isn't one in the 2005 NEC. First I see of it is in 2008 which would explain why the OP used to be able to do it and now he can't.
The reason that this was put into the code is that a lot of people were unaware of the listing prohibition for installing SER cable underground in a conduit.
Probably because it makes no sense, SE is OK for exposed and concealed wet locations but not in a conduit underground.:roll::?:huh:
My guess is that UL never investigated and tested SER cable for used in an underground conduit and that is where the prohibition comes from.
Chris
I really don't care for pulling multiconductor cable into conduit, individual wires is the way to go IMO. They sell USE and XHHW in the regular sizes, so it's a pretty easy substitute for the SER you've been using.
The southwire rep, as I recall stated that ser is fine in the weather but in a conduit underground it is exposed to the minerals etc in the soil. This can cause havoc with the bare aluminum neutral or ground.
Is there an NEC prohibition against pulling a bare AL into an underground conduit?
I know there is a rule about AL GECs but can't recall one for AL EGCs. :?
250.120(B) is as close as you will come and does not specifically prohibit a bare aluminum EGC from being installed in an underground raceway.
Chris
Installed sub-panel to garage. 1.5 pvc with #2 ser inside. legal? done it past 15 years! PAST INSPECTION. Failed on this job per ART # 238?
please advise
250.120(B) is as close as you will come and does not specifically prohibit a bare aluminum EGC from being installed in an underground raceway.
Chris
why would anyone want se aluminum in a conduit underground. .