Hello, we have a700kw generator that will provide 480 volts to transfer switch with a ground and neutral at the distribution/ mcc. The transfer switch has a neutral and ground bonded at the same potential.My question is some guys take the neutral and ground and seperate them at the generator and run a ground , neutral & 3 hots to the transfer switch.Some guys tie the neutral from the gen to the ground and run 3 hots 1 neutral. And other run 3 hots 1 neutral 1 ground from gen to transfer switch. The building is 480volt 3 phase 4 wire. when running 3 hots 1 n 1 ground will the main breaker at the generator trip on fault or the main breaker at the load equipement trip.And what is the best RIGHT WAY to connect this generator, i have my own view what is yours thanks