SmithAndrewR
Member
- Location
- Franklin, CT, USA (Afghanistan)
Here's the background. The facility is a Garage/Storage area with a small office. I have a 4C w/G 4/0 TC-er cable feeding a 225 MB panel being fed from a 250A generator disconnect. All the rules of the outside tap rule apply. An inspector says that due to derating at 80% counting the neutral as a CCC 4/0 is only rated for 184 amps. My response was that the neutral does not count as a CCC as it is a 3p 4w system. He explained to me that computers and fluorescent lamps make it a non-linear load. In my head :rant: of course those are non-linear loads but they only make up a small fraction of the load there are (4) 5hp roll up door motors and and (3) 10 ton ECU's that make up the MAJOR portion of the load. Upon asking him about the motors he told me because of the capacitor for start-up they also had to be counted as non-linear. I've never heard of this. Your thoughts.